To upload Signature loop device data for troubleshooting or diagnostics, you must connect a PC running the 4-CU configuration utility to the 4-CPU module. This process allows you to retrieve mapping and diagnostic information directly from the signaling line circuit (SLC).
Steps:
Connect a USB cable (Type B end) to the J14 USB port on the 4-CPU and the other end to your computer (Page 174) [1].
On the EST4 LCD screen, tap System Info, then select 1 Hour Access Code or 8 Hour Access Code to generate a required code (Page 174) [1].
In the 4-CU software, go to the Home tab, click Enter Access Code, and validate the code from the panel (Page 174) [1].
In the project tree, select the specific Signature loop controller and the SLC you wish to map (Page 174) [1].
On the Home tab, click Mapping Options and select Upload Signature Data from > Panel (Page 174) [1].
Once the progress bar completes, tap Cancel Access Code on the panel LCD to re-activate the Remote Write Lock (Page 174) [1].
Verify with current documentation before making changes.
To upload Signature loop device data for troubleshooting or diagnostics, you must connect a PC running the 4-CU configuration utility to the 4-CPU module. This process allows you to retrieve mapping and diagnostic information directly from the signaling line circuit (SLC).
Steps:
Connect a USB cable (Type B end) to the J14 USB port on the 4-CPU and the other end to your computer (Page 174) [1].
On the EST4 LCD screen, tap System Info, then select 1 Hour Access Code or 8 Hour Access Code to generate a required code (Page 174) [1].
In the 4-CU software, go to the Home tab, click Enter Access Code, and validate the code from the panel (Page 174) [1].
In the project tree, select the specific Signature loop controller and the SLC you wish to map (Page 174) [1].
On the Home tab, click Mapping Options and select Upload Signature Data from > Panel (Page 174) [1].
Once the progress bar completes, tap Cancel Access Code on the panel LCD to re-activate the Remote Write Lock (Page 174) [1].
Verify with current documentation before making changes.