How do I add IDNet devices to an existing 4010ES system?

Simplex4010ESMar 27, 202671 views
0

To add IDNet devices, connect them to the IDNet signaling line circuit (SLC) on the Main System Supply (MSS) or an optional IDNet 2+2 module. The system supports up to 250 devices per SLC and a total of 998 points across the panel (Page 1, 3) [1].

  1. Wiring: Use 18 AWG to 12 AWG wire (Page 3) [1].

For Class B wiring, "T-tapping" is permitted. For Class A, wire from the Primary Terminals (B+, B-) through the devices and back to the Secondary Terminals (A+, A-) (Page 66) [1].

  1. Distance Limits: Ensure the run does not exceed 4,000 ft for up to 125 devices or 2,500 ft for 126-250 devices (Page 3) [1].

  2. Jumpers: Configure module jumpers for the wiring type. Class A uses positions 3-5 and 4-6; Class B uses positions 1-3 and 2-4 (Page 67, 69) [1].

  3. Addressing: Assign a unique address to the device. If using isolators on a Class A loop, address them in sequence starting from the "B" side (Page 67) [1].

  4. Programming: Update the system configuration using the ES Panel Programmer software to recognize the new points (Page 42) [1].

AI-generated — verify against your panel's documentation and applicable codes (NFPA 72, local AHJ).