How do I address devices on the iO1000?
0
The iO1000 uses electronic addressing for all Addressable Signature series devices, meaning there are no physical dip switches or rotary dials to set on the detectors or modules (Page 1) [2].
Addresses are assigned automatically through the panel's automatic device mapping feature or manually using a handheld programmer (Page 2) [3].
Addressing Scheme (per loop):
-
Detectors: Addresses 1 through 125 (Page 124) [1].
-
Modules: Addresses 126 through 250 (Page 124) [1].
To configure or change device settings at the panel:
- Press the Menu button and select Programming.
- Select Advanced Program and enter the Level 2 password.
- Select Device and choose the appropriate SLC loop.
- Enter the device address you wish to configure (1-125 for detectors, 126-250 for modules).
- Modify the device type or label as needed and select Save (Page 124) [1].
Verify with current documentation before making changes.