How do I configure cross-zone verification on the MS-5024 to reduce false alarms?

Fire-LiteMS-5024Mar 19, 2026
0

The MS-5024 does not support cross-zoning; instead, it utilizes a single-zone Alarm Verification feature to reduce false alarms. This feature is only compatible with zones programmed as 2-wire smoke detectors (Page 44) [1].

To configure Alarm Verification:

  1. Enter programming mode and navigate to Address 52.

  2. Enter 1 to enable verification (factory default is '0' for disabled) (Page 44) [1].

  3. Ensure the desired zones (1-5) are programmed as 2-wire smoke detectors at Addresses 57-61 by entering 0 (Page 45) [1].

When enabled, the panel will respond to an initial alarm by removing power for 6 seconds to reset detectors, followed by a 12-second retard period for stabilization. If the same zone alarms again during the subsequent confirmation time, the panel processes a verified alarm (Page 44) [1].

AI-generated — verify against your panel's documentation and applicable codes (NFPA 72, local AHJ).