How do I configure NOTI-FIRE-NET networking on the NFS2-3030, and what is the maximum node count?
0
Standard NOTI-FIRE-NET supports up to 103 nodes (54 if using DVC-EM for network paging), while High-Speed NOTI-FIRE-NET supports up to 200 nodes [1], [4].
Each NFS2-3030 node requires a Network Communication Module (NCM or HS-NCM) and a unique node address [1], [2].
-
Install an NCM or HS-NCM module and connect it to the panel [1], [2].
-
Access the Network Programming menu on the FACP or use VeriFire Tools [1], [3].
-
Enter a unique Node Number (valid range 1-240) [3].
-
Define a Node Label to appear in the System Normal message [3].
-
Select the wiring Style (4 or 7) and set the Threshold (High or Low) for each channel [3].
-
Ensure at least one network display, such as an NCA-2, is present on the network [1].