ESSERFlexESMar 19, 2026
0

To network FlexES panels, you must install an essernet module (62.5 kBd or 500 kBd) and ensure all devices in the network use the same transmission speed (Page 67) [1].

The network supports up to 31 devices (Page 81) [1].

  1. Set the decimal address (1-31) using rotary switches S1 (ones) and S2 (tens) on the module (Page 68) [1].

  2. Slot the module into the basic or expansion module carrier; the bottom slot on the basic carrier is recommended for uniformity (Page 69) [1].

  3. Connect copper wiring to terminals 1 (IN+), 2 (IN-), 3 (OUT+), and 4 (OUT-), attaching cable shielding to the terminal block (Page 69) [1].

  4. Route outward and return lines separately to prevent total connection failure if a cable duct is destroyed (Page 71) [1].

  5. If using fiber optics, install FOC converters (Part No. 784763/4/5) directly on the DIN rail inside the panel (Page 70) [1].

  6. Perform final configuration and commissioning using tools 8000 programming software, version 1.16 or higher (Page 79) [1].