How do I configure the N16 SLC loop for Class A vs. Class B wiring, and what is the maximum loop impedance allowed?

0

To configure the N16 SLC loop, you must program the NFPA class configuration into the panel software; the system will automatically check for a mismatch between the programming and physical wiring (Page 17) [1].

Wiring Configurations:

  • Class B: Use the B+ and B- terminals on the SLM-318. T-tapping is permitted for this configuration (Page 30) [1].

  • Class A or X: Connect the outgoing loop to B+ and B- and the return loop to A+ and A-. T-tapping is not allowed (Page 30) [1].

Maximum Loop Impedance:

  • Standard SLC: 50 ohms maximum per length for Class A/X or per branch for Class B (Page 87) [1], [5].

  • Self-Test Detectors (CLP-2PCB): 35 ohms maximum (Page 19) [1].

  • Self-Test Detectors (Original CLP-PCB): 23 ohms maximum (Page 19) [1].

Additionally, the total capacitance of all SLC wiring must not exceed 0.5 microfarads (Page 20) [1].

AI-generated — verify against your panel's documentation and applicable codes (NFPA 72, local AHJ).