To connect an ACS annunciator to the NFW2-100, wire the EIA-485 communication line to TB9 (terminals B+, A+, B-, and A-) and provide 24 VDC non-resettable power (Page 10, 33) [2], [5].
You must then enable the annunciator and its specific addresses in the FACP programming menu (Page 93) [2].
Addressing Annunciator addresses are point-specific on the NFW2-100 (Page 37) [2]:
Configuration Steps
Enter the Master Programming Level on the FACP.
Navigate to Option Modules and select Annunciators/UDACT (Page 93) [2].
Set ACS Installed to "Yes".
In the ACS Installed Screen, use the number keys to toggle the specific addresses (1-31) you have physically set on your hardware to "Yes" (Page 93) [2].
Ensure the physical DIP switches on the annunciator match the programmed addresses (Page 37) [2].