How do I initiate and conduct a walk test on the NFW2-100 from the front panel keypad?
0
To initiate a walk test on the NFW2-100, navigate to Programming Screen #3 and press 2 for Walktest. This feature allows you to test the system without needing to reset the panel after each device activation (Page 92) [7].
- From Programming Screen #3, press 2 to enter the Walktest menu. 2) Press 1 for a Silent Walktest (NACs off) or 2 for an Audible Walktest (NACs sound). 3) Activate devices throughout the system; the panel will display device info with an asterisk (*) in the time stamp to indicate a test event. 4) Press the Esc key to exit Walktest Mode and return to the Walktest Screen. 5) Press 3 from the Walktest Screen to view the results of the most recent test.