How do I perform a walk test on the FENWALNET 6000 without triggering building notification appliances?
0
To perform a walk test without triggering notification appliances, use the Silent Walk Test mode, which functions identically to an audible test but does not energize programmed outputs (Page 124) [1].
You must physically disconnect all agent-release and pre-action sprinkler circuits before beginning (Page 124) [1].
- Press 0, enter your password, and press Enter.
- Press 4 for the Test-Menu, then press 2 for Walk Test.
- Press 3 to select the Silent Walk Test option.
- Enter the starting and ending SLC addresses (XXX format) and press Enter.
- Press Backspace to exit the menu system.
- Press Acknowledge to silence the buzzer and steady the Trouble LED; the system is now ready for testing (Page 125) [1].