How do I perform a walk test on the MS-5024 without triggering a full alarm?

Fire-LiteMS-5024Mar 19, 20262 views
0

To perform a walk test on the MS-5024, ensure the system has no active alarms and all faults are cleared. This mode allows for testing without triggering the communicator or alarm relays (Page 57) [8], [21].

  1. Press the MODE key.

  2. Enter the 4-digit code 9255 (spells 'WALK').

  3. Press the [ENTER/STORE] key (Page 57) [8].

  4. Test initiating devices; the first activation on a zone sounds NACs for four seconds, while subsequent activations on that zone sound for one second (Page 57) [8].

  5. To exit and return to normal mode, press MODE, enter 6676, and press [ENTER/STORE] (Page 57) [8].

Note that the panel will automatically revert to normal mode if no activity occurs for 60 minutes (Page 57) [8].

AI-generated — verify against your panel's documentation and applicable codes (NFPA 72, local AHJ).