How do I perform a walk test on the MS-9200UDLS?
To perform a walk test on the MS-9200UDLS, navigate to the Walktest menu through either the Programming or Maintenance screens and select between a silent or audible test. This feature allows a single technician to trigger devices without needing to manually reset the panel after each activation.
-
Ensure devices are enabled for testing by setting Walktest to "Yes" in the Edit Detector or Edit Module menus (Page 71) [1].
-
Access the Walktest menu by pressing 2 from Programming Screen #3 or pressing 1 from Maintenance Screen #2 (Page 104, 131) [1].
-
Select the test type: press 1 for a Silent Walktest (logs events only) or 2 for an Audible Walktest (sounds NACs for 4 seconds) (Page 145) [1].
-
Activate devices throughout the system; the panel will display the device information and replace the time colon (:) with an asterisk (*) to indicate a test event (Page 95) [1].
-
Monitor progress by selecting View Walktest Log, View Points (untested), or View Summary from the "Unit In Walktest" screen (Page 104) [1].
-
Exit the test by pressing the Escape key to return to the main Walktest screen, where you can then press 3 to view the final results (Page 105) [1].