The NFS-320 performs automatic detector sensitivity tests every 256 minutes, while the Walk Test uses detector LEDs to provide diagnostic feedback. During a Walk Test, the bicolor or multicolor LEDs on FlashScan detectors blink to indicate the specific device address [1].
While the system can generate Walk Test reports, the specific keypad steps to initiate the test were not found in the provided manuals [1].
Frequency: The control panel automatically tests every installed detector every 256 minutes (Page 58) [1].
Failure Reporting: If a detector fails to meet the required test limits, the panel generates an Auto Test Fail type code (Page 58) [1].
Drift Compensation: The system uses software algorithms to compensate for dust accumulation, allowing it to perform the periodic sensitivity measurements required by NFPA 72 automatically [1].
Maintenance Warnings: If drift compensation reaches its limit, the panel issues three warning levels:** Low Chamber value, Maintenance Alert, and Maintenance Urgent (Page 3) [1].
Note: Manual sections vary between citing two or three maintenance alert levels [1].