To test the NFS2-3030, perform manual operational checks or print results from the Walk Test menu. You must physically disconnect all releasing devices before beginning, as software disables are not a substitute for a physical lockout (Page 58) [1].
Notify the fire department, central station, and facility personnel (Page 58) [1].
Physically disconnect all releasing devices to prevent accidental activation (Page 58) [1].
Press and hold LAMP TEST to verify all display segments and LEDs function (Page 58) [1].
Activate an initiating device and confirm that programmed notification appliances and indicators activate (Page 58) [1].
Reset the panel and repeat for each initiating device on the system (Page 58) [1].
Return all circuits to pretest condition and notify authorities when finished (Page 59) [1].