How do I program and initiate a Self-Test sequence on INSPIRE-compatible detectors from the N16 panel?
To program Self-Test detectors, you must assign the specific FlashScan Type Code (such as FSP-951-SELFT) using VeriFire Tools or the panel's Autoprogram feature [1].
Once programmed, the sequence is initiated through the Self-Test app rather than a direct panel menu command [1].
Programming and Operational Requirements
-
Physical Installation: Install the detector and ensure it is removed for at least 15 seconds to trigger the initialization routine [1].
-
Type Coding: Use the panel touchscreen to perform an Autoprogram or use VeriFire Tools to customize the label and FlashScan code [1].
-
Initialization: Allow approximately 2.5 minutes for the detector to initialize; the LED will latch steady green during this time [1].
-
Power Source: Ensure the system is operating on AC power, as self-tests will not function on secondary (battery) power [1].
-
Loop Status: Be aware that during a self-test, the SLC voltage increases to approximately 29.5VDC and normal device polling is interrupted [1].