How do I program and initiate a Self-Test sequence on INSPIRE-compatible detectors from the N16 panel?

0

To program Self-Test detectors, you must assign the specific FlashScan Type Code (such as FSP-951-SELFT) using VeriFire Tools or the panel's Autoprogram feature [1].

Once programmed, the sequence is initiated through the Self-Test app rather than a direct panel menu command [1].

Programming and Operational Requirements
  1. Physical Installation: Install the detector and ensure it is removed for at least 15 seconds to trigger the initialization routine [1].

  2. Type Coding: Use the panel touchscreen to perform an Autoprogram or use VeriFire Tools to customize the label and FlashScan code [1].

  3. Initialization: Allow approximately 2.5 minutes for the detector to initialize; the LED will latch steady green during this time [1].

  4. Power Source: Ensure the system is operating on AC power, as self-tests will not function on secondary (battery) power [1].

  5. Loop Status: Be aware that during a self-test, the SLC voltage increases to approximately 29.5VDC and normal device polling is interrupted [1].

AI-generated — verify against your panel's documentation and applicable codes (NFPA 72, local AHJ).