How do I program the three NAC circuits on the Aegis 2.0 for pre-release alarm versus post-release notification?

KiddeAegis 2.0Mar 19, 2026
0

Each NAC on the AEGIS 2.0 is independently configurable for Pre-Release and Releasing (post-release) conditions via the system configuration menu (Page 21) [1].

By default, the panel is factory-programmed with NAC 2 for Pre-Release and NAC 3 for Releasing (Page 90) [1].

To customize these, follow these steps: 1. Define the NAC relationship to the Agent Release Circuits (ARCs) using configuration settings 24 (NAC 1), 25 (NAC 2), or 26 (NAC 3) (Page 57) [1].

  1. Program the Pre-Release notification pattern using setting 28 (NAC 1), 31 (NAC 2), or 34 (NAC 3) (Page 58, 60) [1].

  2. Program the Releasing notification pattern using setting 29 (NAC 1), 32 (NAC 2), or 35 (NAC 3) (Page 58, 60) [1].

  3. For each state, select a pattern (0-A) such as Temporal, Steady, or Intelligent Synchronization; select 'C' (NAC Off) if notification is not required for that specific condition (Page 58) [1].

AI-generated — verify against your panel's documentation and applicable codes (NFPA 72, local AHJ).