How do I program zones and assign addressable points to zones using the MS-5024 front panel keypad?
The MS-5024 is a conventional panel and does not support addressable points; instead, you program the function of its five hardware zones. To configure these, you must enter Program Mode and assign function codes to addresses 57 through 61. 1. Press MODE, enter 7764, and press [ENTER/STORE] to enter Program Mode (Page 66) [1].
-
Enter the address for the zone you are configuring: 57 (Zone 1), 58 (Zone 2), 59 (Zone 3), 60 (Zone 4), or 61 (Zone 5) (Page 45) [1].
-
Enter the function code: 0 (Smoke), 1 (Pull), 2 (N.O. Contact), 3 (Supervisory), or 4 (Supervisory Auto) (Page 41) [1].
-
For Zone 3, you may also select 5 (Silenceable Waterflow) or 6 (Non-silenceable Waterflow) (Page 41) [1].
-
Press [ENTER/STORE] to save the selection and move to the next address (Page 44) [1].
-
Press MODE, enter 6676, and press [ENTER/STORE] to return to Normal Mode (Page 82) [1].