How do I set zone types on the MS-5024?
0
To set zone types on the MS-5024, you must enter programming mode and assign a function code to the specific memory address for each zone. Use addresses 57 through 61 to program zones 1 through 5 respectively [6], [13].
-
Press MODE, enter the code 7764, and press ENTER to access programming [4].
-
Navigate to the address for the zone you wish to configure:** 57** (Zone 1), 58 (Zone 2), 59 (Zone 3), 60 (Zone 4), or 61 (Zone 5) [13].
-
Enter the digit corresponding to the desired Zone Function:
- 0: 2-wire smoke detector (factory default)
- 1: Pull Station
- 2: Normally Open Contact Device
- 3: Supervisory
- 4: Supervisory, auto-resettable [6].
-
For Zone 3 only, you may also enter 5 for Waterflow (silenceable) or 6 for Waterflow (non-silenceable) [12], [13].
-
Press ENTER/STORE to save the entry.