How do I troubleshoot a ground fault on the NFS2-640 SLC loop?
To troubleshoot a Ground Fault Loop x on the NFS2-640, you must physically locate and repair the point where the SLC wiring is contacting earth ground (Page 75) [1].
The panel will display this as a latching trouble, meaning it will remain on the screen even after the fault is cleared until the system is manually reset (Page 75) [1].
-
Identify the affected loop (Loop 1 or Loop 2) from the specific error message on the panel display (Page 75) [1].
-
Verify that all mounting holes of the NFS2-640 chassis are secured with a screw or standoff to ensure proper Earth Ground continuity (Page 4) [1].
-
Check the D55 Main SLC Ground Fault LED or D72 General Board Ground Fault LED on the CPU to confirm if the fault is on the SLC or the internal board (Page 5) [1].
-
Inspect field wiring for pinched conductors, moisture in junction boxes, or wires touching the conduit.
-
If the loop is configured for Style 6 or Style 7, the panel will continue to communicate with devices by driving both ends of the loop while the fault exists (Page 75) [1].
-
Once the physical fault is repaired, press the RESET button to clear the trouble from the display (Page 75) [1].