How do I wire and configure ACM-30 annunciators on the N16, and what is the maximum number supported?

0

The N16 supports a maximum of 80 ACM-30 annunciators connected via the AIO Bus (Page 1) [1].

Wiring requires four wires: two for EIA-485 communications (twisted pair) and two for filtered, non-resettable 24 VDC power (Page 1, 38) [1].

Wiring and Configuration Steps
  1. Power Down: Remove all AC and DC power from the FACP before installation (Page 37) [1].

  2. Set Addressing: Use the rotary dial on each device to set a unique address between 01 and 15; address 00 is invalid (Page 37) [1].

  3. Main Bus: Connect the FACP AIO-BUS to connector P6 on the ACM-30 configured as a router (Page 38) [1].

  4. Peripherals: Use connectors P3 or P4 with ribbon cables (6-inch for same row, 48-inch for different rows) to connect up to 15 peripheral ACM-30s to each router (Page 38) [1].

  5. Enrollment: On N16 panels version 6.x or higher, use the ENROLL DEVICES touch point on the display to automatically recognize devices on the bus [1].

  6. Programming: Use VeriFire Tools to customize buttons and LEDs in either Independent Mode (60 points) or Cooperate Mode (Page 1, 2) [1].

System Capacity
FeatureLimit
Total ACM-30s per N1680 units (Page 1) [1]
Max Routers10 addresses (Page 42) [1]
Peripherals per Router15 units (Page 42) [1]
Max Devices per AIO Circuit40 units (Page 37) [1]
Mapping Limit (No SWIFT)32 units per node (Page 42) [1]
Mapping Limit (With SWIFT)8 units per node (Page 42) [1]
AI-generated — verify against your panel's documentation and applicable codes (NFPA 72, local AHJ).