How do I wire and configure ACM-30 annunciators on the N16, and what is the maximum number supported?
The N16 supports a maximum of 80 ACM-30 annunciators connected via the AIO Bus (Page 1) [1].
Wiring requires four wires: two for EIA-485 communications (twisted pair) and two for filtered, non-resettable 24 VDC power (Page 1, 38) [1].
Wiring and Configuration Steps
-
Power Down: Remove all AC and DC power from the FACP before installation (Page 37) [1].
-
Set Addressing: Use the rotary dial on each device to set a unique address between 01 and 15; address 00 is invalid (Page 37) [1].
-
Main Bus: Connect the FACP AIO-BUS to connector P6 on the ACM-30 configured as a router (Page 38) [1].
-
Peripherals: Use connectors P3 or P4 with ribbon cables (6-inch for same row, 48-inch for different rows) to connect up to 15 peripheral ACM-30s to each router (Page 38) [1].
-
Enrollment: On N16 panels version 6.x or higher, use the ENROLL DEVICES touch point on the display to automatically recognize devices on the bus [1].
-
Programming: Use VeriFire Tools to customize buttons and LEDs in either Independent Mode (60 points) or Cooperate Mode (Page 1, 2) [1].
System Capacity
| Feature | Limit |
|---|---|
| Total ACM-30s per N16 | 80 units (Page 1) [1] |
| Max Routers | 10 addresses (Page 42) [1] |
| Peripherals per Router | 15 units (Page 42) [1] |
| Max Devices per AIO Circuit | 40 units (Page 37) [1] |
| Mapping Limit (No SWIFT) | 32 units per node (Page 42) [1] |
| Mapping Limit (With SWIFT) | 8 units per node (Page 42) [1] |