Common SLC loop troubles on the 6820 include DBL ADDR, Missing, GROUND FAULT, and SLC Loop Shorted. To diagnose these conditions, follow the specific procedures for each message:**
DBL ADDR (Double Address): This occurs when an address is assigned to more than one detector. Correct the address following the SK and SD device procedures in the SLC Wiring Manual (Page 149) [1].
Missing: This indicates devices are not being recognized. Verify hardware connections, wiring polarity, and ensure devices are connected to the SLC OUT terminals (not SLC IN) on expander modules (Page 149) [1].
GROUND FAULT: This occurs when the panel senses current flowing to earth ground. Isolate the fault by removing wiring connections one at a time, pausing at least five seconds between each, until the fault clears. Note that a computer connected via USB or serial cable will also trigger this message (Page 149) [1].
SLC Loop Shorted: This indicates a short circuit on the loop (Page 148) [1].
SLC Impedance Troubleshooting If devices are missing, use this procedure to verify loop integrity: