The Simplex 4010ES supports four on-board notification appliance circuits (NAC1 through NAC4) (Page 64) [1].
NAC Specifications: Each circuit is rated for 3 A (8 A total) for Special Application using listed appliances, or 2 A per circuit (4 A total) for Regulated 24 VDC using non-listed appliances (Page 24, 25) [1].
The nominal voltage is 24 VDC with 2 Vp-p maximum ripple (Page 63) [1].
Each circuit supports up to 70 appliances, and Class B wiring requires a 10 kOhm, 1/2 W end-of-line resistor (Page 64, 65) [1].
The Simplex 4010ES supports four on-board notification appliance circuits (NAC1 through NAC4) (Page 64) [1].
NAC Specifications: Each circuit is rated for 3 A (8 A total) for Special Application using listed appliances, or 2 A per circuit (4 A total) for Regulated 24 VDC using non-listed appliances (Page 24, 25) [1].
The nominal voltage is 24 VDC with 2 Vp-p maximum ripple (Page 63) [1].
Each circuit supports up to 70 appliances, and Class B wiring requires a 10 kOhm, 1/2 W end-of-line resistor (Page 64, 65) [1].