To test the manual release without discharging agent, you must isolate the system and verify the panel's response to the input. 1. Notify personnel and monitoring stations that the system is under test (Page 69) [1].
-
Press the Output Disable switch to prevent NAC and agent release activation (Page 69) [1].
-
Physically disconnect all wiring from the release-circuit terminals (TB4) and remove control heads from discharge valves (Page 69, 126) [1].
-
Bypass auxiliary functions like facility power shutoff (Page 69) [1].
-
Activate the manual release station and confirm the panel indicates Pre-Release and Releasing states (Page 126) [1].
-
Perform a System Reset and restore all connections to return to normal operation (Page 62, 175) [1].