What is the procedure to program individual NAC circuits on the FX-10 for Genesis protocol versus standard temporal output?
To program NAC circuits on the FX-10, you must access the panel programming menu and assign specific values to the NAC Type option for each circuit.
-
Enter the programming menu and select the NAC Type option (Step 21) (Page 42) [1].
-
Identify the NAC being programmed by its Trouble LED; while NAC 1 is selected by default, you can select a different NAC by pressing that circuit's Disable button (Page 41) [1].
-
To configure Genesis protocol, select GENESIS for synchronized continuous signals with horn-only silence, or GENESIS (AV Sil) if both horns and strobes must be silenced (Page 41) [1].
-
To configure Standard Temporal, select Temporal (3-3-3), which outputs an unsynchronized 24-volt temporal signal for appliances designed to output a steady tone (Page 41) [1].
-
Enter the value for each NAC before proceeding to the next programming option (Page 41) [1].