What is the process to perform a one-person walk test on the FX-10?
To perform a walk test on the FX-10, ensure the panel has no active alarm or supervisory events. This procedure allows a single technician to test devices as the panel automatically resets the circuit after each activation. 1. Press the Walk Test button once for an audible test (LED turns on) or twice for a silent test (LED flashes) (Page 63) [1].
-
Press the Disable button for the specific IDC you want to test (Page 63) [1].
-
Activate the initiating device; in audible mode, the NACs will sound a number of times equal to the zone number (Page 62) [1].
-
Restore the device to its normal state. 5. Wait approximately 8 seconds for the panel to automatically reset the IDC before testing the next device (Page 62) [1].
-
Press the Walk Test button a third time to exit the test mode (Page 62) [1].